Is there a requirement for protection of the meter pans and disconnects?
110.27 Guarding of Live Parts.
(B) Prevent Physical Damage. In locations where electrical
equipment is likely to be exposed to physical damage,
enclosures or guards shall be so arranged and of such
strength as to prevent such damage.
230.50 Protection Against Physical Damage.
(A) Underground Service-Entrance Conductors. Underground
service-entrance conductors shall be protected
against physical damage in accordance with 300.5.
(B) All Other Service-Entrance Conductors. All other
service-entrance conductors, other than underground ser
vice entrance conductors, shall be protected against physical
damage as specified in 230.50(B)(1) or (B)(2).
(1) Service-Entrance Cables. Service-entrance cables,
where subject to physical damage, shall be protected by any
of the following:
(1) Rigid metal conduit
(2) Intermediate metal conduit
(3) Schedule 80 PVC conduit
(4) Electrical metallic tubing
(5) Reinforced thermosetting resin conduit (RTRC)
(6) Other approved means
(2) Other Than Service-Entrance Cables. Individual open
conductors and cables, other than service-entrance cables,
shall not be installed within 3.0 m (10 ft) of grade level or
where exposed to physical damage.
Exception: Type MI and Type MC cable shall be permitted
within 3.0 m (10 ft) of grade level where not exposed to
physical damage or where protected in accordance with
300.5(D).-
240.24 Location in or on Premises.
(C) Not Exposed to Physical Damage. Overcurrent devices
shall be located where they will not be exposed to
physical damage.