wwhitney
Senior Member
- Location
- Berkeley, CA
- Occupation
- Retired
This change better reflects my understanding that Articles 225 and 230 are disjoint, and that neither one regulates forms of supply to a building subject to the other Article.
A corollary to that would be that a building can be supplied by one service, and one branch circuit or feeder, without restriction. That's my understanding of the current state of play, but it has been suggested that the intention is to restrict a building to one source of supply of any type, absent one of the conditions listed.
So if that's really the case, and if that's really a good idea, a different PI would be appropriate to make that happen clearly. Please let me know if you think that's the intention and/or if that's a good idea. I already know what changes would be required to 225.30 and 230.2, so it's just a matter of writing the substantiation.
225.30 Number of Branch Circuit or Feeder Supplies.
Statement of Problem and Substantiation for Public Input
In keeping with the scope of Article 225, this change clarifies that the supplies covered by 225.30 are only branch circuits and feeders, and that that 225.30 does not regulate services in any way. As the wording currently stands, the subsequent phrase "shall be supplied by only one feeder or branch circuit" can be interpreted to preclude additional supply by a service.
A corollary to that would be that a building can be supplied by one service, and one branch circuit or feeder, without restriction. That's my understanding of the current state of play, but it has been suggested that the intention is to restrict a building to one source of supply of any type, absent one of the conditions listed.
So if that's really the case, and if that's really a good idea, a different PI would be appropriate to make that happen clearly. Please let me know if you think that's the intention and/or if that's a good idea. I already know what changes would be required to 225.30 and 230.2, so it's just a matter of writing the substantiation.
225.30 Number of Branch Circuit or Feeder Supplies.
Statement of Problem and Substantiation for Public Input
In keeping with the scope of Article 225, this change clarifies that the supplies covered by 225.30 are only branch circuits and feeders, and that that 225.30 does not regulate services in any way. As the wording currently stands, the subsequent phrase "shall be supplied by only one feeder or branch circuit" can be interpreted to preclude additional supply by a service.