wwhitney
Senior Member
- Location
- Berkeley, CA
- Occupation
- Retired
A couple technical corrections so the literal meaning of the section matches the common understanding.
Cheers, Wayne
240.4 Protection of Conductors Circuit conductors, other than flexible cords, flexible cables, and fixture wires, shall be protected against overcurrent in accordance with their ampacities specified in 310.14, unless otherwise permitted or required in 240.4(A) through (H).
Statement of Problem and Substantiation for Public Input
Overcurrent devices are not installed in equipment grounding conductors and other conductors that are not part of a circuit. So while obvious, that distinction should be made explicit.
Cheers, Wayne
240.4 Protection of Conductors Circuit conductors, other than flexible cords, flexible cables, and fixture wires, shall be protected against overcurrent in accordance with their ampacities specified in 310.14, unless otherwise permitted or required in 240.4(A) through (H).
Statement of Problem and Substantiation for Public Input
Overcurrent devices are not installed in equipment grounding conductors and other conductors that are not part of a circuit. So while obvious, that distinction should be made explicit.