wwhitney
- Berkeley, CA
- Retired
Another. Cheers, Wayne
New paragraph 240.4(I) (with the opening of 240.4 updated to reference the new paragraph):
(I) Neutral Conductors. Neutral conductors sized according to their load calculated per 220.61 shall be permitted to be protected against overcurrent by the overcurrent protective devices for their associated ungrounded conductors.
Statement of Problem and Substantiation for Public Input
220.61 permits a neutral conductor's size to be reduced relative to its corresponding ungrounded circuit conductors, and this is common industry practice. However, 240.4 requires that circuit conductors be protected against overcurrent in accordance with their ampacity, and it currently provides no allowance for a reduced size neutral. As such this common industry practice is in violation of 240.4 as currently written. This change removes this presumably unintended oversight.