This PI just changes the title of Table 310.12(A) to exclude conductors limited to 60C ampacity.
Cheers, Wayne
Table 310.12(A) Single-Phase Dwelling Services and Feeders For Conductors Not Limited to 60C Ampacity
Statement of Problem and Substantiation for Public Input
As currently written, Table 310.12 would allow #4 NM cable to be utilized for a 100A feeder "supplying the entire load associated with a one-family dwelling," since there is no restriction on the wiring method mentioned. However, the ampacity of #4 NM cable is limited to 70A per 334.80, so this would provide a ratio of ampacity to rating of 70%, much less than the 83% specified in section 310.12.
Thus it is my understanding that the use of Table 310.12 is intended to be limited to wiring methods that can make use of the 75C ampacity columns in Tables 310.16 et al. Therefore that restriction needs to be placed on Table 310.12. Since multiple paragraphs refer to Table 310.12, putting the restriction in the table heading seems simplest.
Cheers, Wayne
Table 310.12(A) Single-Phase Dwelling Services and Feeders For Conductors Not Limited to 60C Ampacity
Statement of Problem and Substantiation for Public Input
As currently written, Table 310.12 would allow #4 NM cable to be utilized for a 100A feeder "supplying the entire load associated with a one-family dwelling," since there is no restriction on the wiring method mentioned. However, the ampacity of #4 NM cable is limited to 70A per 334.80, so this would provide a ratio of ampacity to rating of 70%, much less than the 83% specified in section 310.12.
Thus it is my understanding that the use of Table 310.12 is intended to be limited to wiring methods that can make use of the 75C ampacity columns in Tables 310.16 et al. Therefore that restriction needs to be placed on Table 310.12. Since multiple paragraphs refer to Table 310.12, putting the restriction in the table heading seems simplest.