wwhitney
- Berkeley, CA
- Retired
Sharpen (make more precise) the language used in the exception.
Cheers, Wayne
2) Selection of Ampacity. Where more than one ampacity applies for a given circuit length, the lowest value shall be used.
Exception: Where different ampacities resulting from ampacity adjustment and/or correction apply to portions of a circuit, the higher ampacity shall be permitted to be used if the total portion(s) of the circuit with lower ampacity does not exceed the lesser of 3.0 m (10 ft) or 10 percent of the total circuit.
Statement of Problem and Substantiation for Public Input
Different ampacities can result from a variety of differences: different ambient temperature, a different number of current carrying conductors, a change in conductor material, or a change in conductor size. To my understanding, this exception is intended only for the first two reasons, a change in the ampacity adjustment or correction along the length of a circuit. The proposed language makes it clear that changing conductor size or conductor material is not covered by the exception.
Without this change, a change in conductor size could reasonably be considered to be covered by the exception. So for example 10' of #8 Cu conductor could be inserted into a 100' long 125A feeder, and the exception as currently worded would allow the use of the higher 125A ampacity for the entire circuit.
Cheers, Wayne