wwhitney
Senior Member
- Location
- Berkeley, CA
- Occupation
- Retired
More ambiguity removal. Cheers, Wayne
(1) Without Adjustment and Correction Factors.
The minimum conductor size with an ampacity not less than the maximum currents calculated in 690.8(A) multiplied by 125 percent.
Exception: Circuits containing an assembly, together with its overcurrent device(s), if any, that is listed for continuous operation at 100 percent of its rating shall be permitted to be used at 100 percent of its rating.
Statement of Problem and Substantiation for Public Input
Clarify that in the case a circuit has no overcurrent devices, e.g. as allowed under 690.9(A)(1), the exception may still be used as long as the rest of the equipment in the circuit is listed for continuous operation at 100 percent of its rating.
(1) Without Adjustment and Correction Factors.
The minimum conductor size with an ampacity not less than the maximum currents calculated in 690.8(A) multiplied by 125 percent.
Exception: Circuits containing an assembly, together with its overcurrent device(s), if any, that is listed for continuous operation at 100 percent of its rating shall be permitted to be used at 100 percent of its rating.
Statement of Problem and Substantiation for Public Input
Clarify that in the case a circuit has no overcurrent devices, e.g. as allowed under 690.9(A)(1), the exception may still be used as long as the rest of the equipment in the circuit is listed for continuous operation at 100 percent of its rating.