I'm listing only the new item I propose, rather than reiterate the whole section.
Cheers, Wayne
(7) Where a busbar has only three connections to it, counting the primary power source, each connection shall be protected by an overcurrent device whose rating does exceed the busbar ampere rating. Where the distribution equipment has provisions for a fourth connection, a permanent warning label shall be applied that displays the following or equivalent wording:
WARNING:
EQUIPMENT FED BY MULTIPLE SOURCES. DO NOT MAKE ADDITIONAL CONNECTIONS TO BUSBAR.
Statement of Problem and Substantiation for Public Input
Under the conditions specified in the proposed text, it is impossible to overload the busbar: By Kirkoff's Law, current in must equal current out. So if two of the three connections are acting as power sources (current in), the other must be acting as the sole load (current out), and the current out is suitably limited by its overcurrent device. While if only one of the connections is acting as a power source, the current in is limited as usual.
Also, please note that the second sentence of 2020 NEC 705.12 began "Where distribution equipment or feeders are fed simultaneously by a primary source of electricity and one or more other power source and are capable of supplying multiple branch circuits or feeders, or both." This wording limits the scope of the rest of 705.12 to equipment capable of at least 4 connections: at least two for the power sources, and at least two for the multiple branch circuits/feeders.
However, in the 2023 NEC and the corresponding sentence in 705.12, the qualifier "and are capable of supplying multiple branch circuits or feeders, or both" was omitted. This removed the exemption for equipment only capable of 3 connections.
Therefore, this proposed addition restores the longstanding allowance for equipment capable of only 3 connections. It also extends the allowance to equipment capable of more than 3 connections, so long as a suitable warning is posted, in accordance with the other items in this section.
Cheers, Wayne
(7) Where a busbar has only three connections to it, counting the primary power source, each connection shall be protected by an overcurrent device whose rating does exceed the busbar ampere rating. Where the distribution equipment has provisions for a fourth connection, a permanent warning label shall be applied that displays the following or equivalent wording:
WARNING:
EQUIPMENT FED BY MULTIPLE SOURCES. DO NOT MAKE ADDITIONAL CONNECTIONS TO BUSBAR.
Statement of Problem and Substantiation for Public Input
Under the conditions specified in the proposed text, it is impossible to overload the busbar: By Kirkoff's Law, current in must equal current out. So if two of the three connections are acting as power sources (current in), the other must be acting as the sole load (current out), and the current out is suitably limited by its overcurrent device. While if only one of the connections is acting as a power source, the current in is limited as usual.
Also, please note that the second sentence of 2020 NEC 705.12 began "Where distribution equipment or feeders are fed simultaneously by a primary source of electricity and one or more other power source and are capable of supplying multiple branch circuits or feeders, or both." This wording limits the scope of the rest of 705.12 to equipment capable of at least 4 connections: at least two for the power sources, and at least two for the multiple branch circuits/feeders.
However, in the 2023 NEC and the corresponding sentence in 705.12, the qualifier "and are capable of supplying multiple branch circuits or feeders, or both" was omitted. This removed the exemption for equipment only capable of 3 connections.
Therefore, this proposed addition restores the longstanding allowance for equipment capable of only 3 connections. It also extends the allowance to equipment capable of more than 3 connections, so long as a suitable warning is posted, in accordance with the other items in this section.