If you go to the "search" feature of this forum and do a search for "42 circuits per panel" you'll find several interesting comments on this subject. Here are a few comments from regular contributors :
408.4 Classification of Panelboards. Panelboards shall be classified for the purposes of this article as either lighting and appliance branch-circuit panelboards or power panelboards, based on their content. A lighting and appliance branch circuit is a branch circuit that has a connection to the neutral of the panelboard and that has overcurrent protection of 30 amperes or less in one or more conductors.
(A) Lighting and Appliance Branch-Circuit Panelboard.
A lighting and appliance branch-circuit panelboard is one having more than 10 percent of its overcurrent devices protecting lighting and appliance branch circuits.
(B) Power Panelboard. A power panelboard is one having 10 percent or fewer of its overcurrent devices protecting lighting and appliance branch circuits.
408.15 Number of Overcurrent Devices on One Panelboard. Not more than 42 overcurrent devices (other than those provided for in the mains) of a lighting and appliance branch-circuit panelboard shall be installed in any one cabinet or cutout box.
A lighting and appliance branch-circuit panelboard shall be provided with physical means to prevent the installation of more overcurrent devices than that number for which the
panelboard was designed, rated, and approved.
For the purposes of this article, a 2-pole circuit breaker shall be considered two overcurrent devices; a 3-pole circuit
breaker shall be considered three overcurrent devices.
--------------------
Pierre Belarge
Instructor & Industry Advocate, NY
***************************************************
According to Anthony Montuori, Chief Inspector for the NY Board of Fire Underwriters, a lighting panel was restricted to 42 circuits as the result of a 1928 fire at the Waldorf Astoria. The cause of that fire was determined to be from an electric panel wired with type "R" cable whose overall heat load caused the fire. The electrical apparatus of the time could safely handle a 42 circuit panel while a larger panel could not.
From this site: Tradeslang.com
--------------------
Bryan Holland
Electrical Council of Florida
City of North Port Electrical Inspector
*********************************************
If you stop and think about the logic of the 42 circuit rule, we all know how tight the trough area can be inside a breaker panel that is loaded with 40 or 42 circuits. Can you imagine what it would be like if we were permitted to install piggy backed breakers in all the positions and thereby creating an 80 or 84 circuit panel? Forget about the phase conductors for a moment, where do you land the neutrals and EGC's. How about the heat generated from all the circuit wires inside tha panel?