Mattlong317
- Beech Grove, Indiana
Hey guys,
Almost 20 year experience guy here, but ran into a situation today that normally I would not think about doing, any and all help appreciated.
At an estimate today , in a very huge home, but outdated , the system was a weird mix of fuse disconnects , troughs, and breakers. Looked like commercial guys did work to the home post disable disconnect and updated to half breaker half fuse system. Very weird to me. Anyway homeowner ( H.O. ) has 20kw furnace , with only one circuit powering it , and jumpers from
60A breaker to 60A breaker in the furnace. 220V CIRCUIT BTW. Normally this requires 2 60A circuits to run the 20kw furnace. The furnace will not run correctly , keeps blowing fuses. My partner swears that insufficient power when motor starts can blow the fuses. Problem lies in that in the H.O electrical system no room for any tandem breakers and only 1 fuse disconnect opening . So question is , if we add another 60 amp circuit , can the original 60 Amp circuit, and our new 60 Amp circuit be pigtailed in the load center and be powered under the one fuse location ? ?
Also after doing some research , could this be a 25kw furnace with a 5kw element disconnected, and we may have mistaken #4 conductors that should have 80Amp fuses instead of 60Amp fuses, for 6 gauge wire, thus making the jumpers from breaker to breaker in furnace okay , and H.O. has wrongly been installing 60 Amp fuses ? I read a similar example online today.
Would the smartest option go with normal routine install 2 60Amp circuits , and pigtail them in the fuse disconnect , near main load center ? I have always understood " multitapping circuits " Is a code violation , but from research today I find that if breaker is designed for 2 conductors , or circuits are pigtails, tapping 2 circuits into one breaker/ fuse is perfectly fine??
Any and all help is highly appreciated.