480sparky said:But I found this today, in my newly-acquired 1943 NEC:
iwire said:Cool, congratulations.![]()
It has been said before that it was the war and it's copper restrictions that was the reason for the 3 wire feeds to ranges and dryers.
So can I ask if the 1943 allows ranges and dryers to be grounded via the neutral?
And do you have an earlier NEC?
480sparky said:I know it's been hashed before, and most here agree that pigtailing is not an NEC requirement on receptacles (other than for MWBCs).
But I found this today, in my newly-acquired 1943 NEC:
![]()
So there it is, right from 'the horse's mouth'.
Jim W in Tampa said:That does not make it a quality job just a legal one.If your working under me get use to pigtails fast.
Jim W in Tampa said:That does not make it a quality job just a legal one.If your working under me get use to pigtails fast.
480sparky said:I pigtail no matter what. And I abhor those who don't. I just posted this to 'set the record straight'.
Personally, I would really like to know the true cross-sectional area (cmil) of those little tabs you break off on a receptacle. Is it anywhere near even a 14AWG?
The better back-wire pressure-plate receptacles I've seen allow two wires per screw. So if you daisy-chain your conductors under the same screw, the connection doesn't depend on the little tab.480sparky said:Personally, I would really like to know the true cross-sectional area (cmil) of those little tabs you break off on a receptacle. Is it anywhere near even a 14AWG?
wwhitney said:The better back-wire pressure-plate receptacles I've seen allow two wires per screw. So if you daisy-chain your conductors under the same screw, the connection doesn't depend on the little tab.
Yours, Wayne
480sparky said:I pigtail no matter what. And I abhor those who don't. I just posted this to 'set the record straight'.
Personally, I would really like to know the true cross-sectional area (cmil) of those little tabs you break off on a receptacle. Is it anywhere near even a 14AWG?
Jim W in Tampa said:I seen a fire start over using them screws to feed thru.By luck i just happened to be there and quickly killed breakers and put flame out with water.Was an all wood cheeky hut.Rewired the place the next week.Many things are legal but bad practice.Will admitt on track homes we had no choice but to back stab to keep price down.
Jim W in Tampa said:Could you post the info on one of them ? 2 wires under one screw ? i sure hope your joking
Ok thanks Bob ,i wasnt reading right.iwire said:No he is not joking, think of the terminal on a Square D breaker, it is a screw with a square 'washer' that allows you to place one conductor under each side of the screw. The conductors do not wrap around the screw.
Jim W in Tampa said:I seen a fire start over using them screws to feed thru.By luck i just happened to be there and quickly killed breakers and put flame out with water.Was an all wood cheeky hut.Rewired the place the next week.Many things are legal but bad practice.Will admitt on track homes we had no choice but to back stab to keep price down.
acrwc10 said:But a beat up price gets a beat up job.
480sparky said:So if the load that 'caused the fire' was plugged into the receptacle that caught fire, it wouldn't have made any difference if there was no pigtail. It wasn't the fact that it wasn't pigtailed, it was due to the termination either was poorly done originally or came loose for some reason over time. I'm not defending not pigtailing here, just pointing out that this instance has nothing to do with pigtailing.
iwire said:I will give you an Amen to that.![]()
If the customer fought to get the price down they do not deserve a Cadillac.
I seen a fire start over using them screws to feed thru. By luck i just happened to be there and quickly killed breakers and put flame out with waterways an all wood cheeky hut. Rewired the place the next week. Many things are legal but bad practice. Will admit on track homes we had no choice but to back stab to keep price down.
Some times I pigtail, some times I don't.
acrwc10 said:Can I get an AMEN from the chior ? I have done very few jobs where I had to "cut corners" in a code leagal way. But a beat up price gets a beat up job. I read recently where a financial advisor was saying "the job you have to fight to get by price cutting , is a job you don't want"