jgriffin02
Member
A friend is doing a major rewire on his house. He has no multiwire circuits. He wired the outlets using the side terminals as a pass-through rather than using pigtails. The circuit is #12 at 20 amps. The outlets are 15 amp. The building inspector doesn't like that he didn't pigtail and said that the 15 amp outlets are no good for 20 amp pass through. My friend contacted Leviton and they sent him documentation that shows that the outlets are rated at 15 amp supply, 20 amp pass through.
I cannot find in the code were it explicitly says that the device can be wired for pass through, only the implication that if the circuit is multiwire, the grounded neutral cannot be wired pass through.
Anyone know the NEC reference that would make this inspector happy (or not).
I cannot find in the code were it explicitly says that the device can be wired for pass through, only the implication that if the circuit is multiwire, the grounded neutral cannot be wired pass through.
Anyone know the NEC reference that would make this inspector happy (or not).