Does the NEC allow unprotected SE cable from the outside meter to be run in the hollow space of the walls in a dwelling before it reaches the overcurrent protection?
230.70(A)(1)(1) Readily Accessible Location. The service disconnecting means shall be installed at a readily accessible location either outside of a building or structure or inside nearest the point of entrance of the service conductors.
I thought we were talking about Service Entrance Cable for non-fused service conductors. How does this section apply ?Article 338.10(B)(4)(a) sends you to Article 334 NM-B. Section 334.10 Uses Permitted(A)(1) for both exposed and concealed work
I thought we were talking about Service Entrance Cable for non-fused service conductors. How does this section apply ?
Please forgive me, I'm really not out to break anyone's chops here but I don't think we're all on the same page regarding this subject. The OP was asking about that unprotected piece of SEU cable from the meter to the first over-current device. We're not talking about SE cable used for branch circuits or protected feeders. So far I think Roger has the best answer.We are, but SE cable has the same restrictions as NM cable. 9Follow the Code references)
Your code references would be correct if we were talking about branch circuits or feeders however, the disscussion is about service entrance conductors as Goldstar and Augie point out and the rules are the same for all wiring methods.We are, but SE cable has the same restrictions as NM cable. 9Follow the Code references)