rckstr
Member
- Location
- Memphis, Tn U.S.A.
480V 3PH 70A ckt feeds six MOV’s (Motor Operated Valves) located in tank farm of petroleum storage facility. The 70A breaker is tapped from an 800A fused disconnect fed directly from local utility (pole mount transformers). #1 THHN runs between MOV disconnects (mostly underground conduit). Each disconnect has a 20A breaker close to the MOV. At the farthest two MOVs (800ft) we get 2 pin holes blown through the insulation about 1 foot apart. This is every few weeks for the last six months. System ran for one year prior with no problems. Recording meter captures a 15,000hz frequency surge with no significant change in voltage or current at the time of each event. Each MOV has a control transformer and forward/reversing starter, but this happens even when none of the MOV’s are in use. We have swabbed the conduits several times with wire ease and rags. We removed the #12 from the load side of the disconnects and pulled #6 to the MOV’s with the same result. Have not used oscilloscope, but imagine we are getting such an ugly sine wave it appears as 15kHz to the recording meter. There are no VFDs within 2000ft. I see no switching power supplies. All the area lighting appear to be functioning properly. The only thing resembling witchcraft close by is an ancient cathodic grounding system. As an electrician the only formulas I deal with involving frequency are about reactance: but we never see a voltage or current anomaly.......Considering abandoning search for the source and pursuing mitigation. Thinking: isolation transformers, TVSS with filtering, and/or XHHW wire….What say ye?