Hello,
So 250.66 says that if you have a pipe electrode then the size of the GEC does not need to be >6AWG (similar to ground rod). However, I have seen that people require a #4AWG to a water pipe for a 200A service. Is a water pipe a special type of pipe that needs to be sized to the full size of 250.66? If you do have a number #4AWG to a water pipe, I assume you can connect a rebar #4AWG to it as a location for its boding jumper to terminate as permitted by 250.68( C ) (1)?
So 250.66 says that if you have a pipe electrode then the size of the GEC does not need to be >6AWG (similar to ground rod). However, I have seen that people require a #4AWG to a water pipe for a 200A service. Is a water pipe a special type of pipe that needs to be sized to the full size of 250.66? If you do have a number #4AWG to a water pipe, I assume you can connect a rebar #4AWG to it as a location for its boding jumper to terminate as permitted by 250.68( C ) (1)?