Installing a 200a service, and a 100a remote distribution panel.
Trying to make sure I used right tables to get my pipe fill calculations.
The service entrance conductors will be 3/0 cu thhn/thwn. I used value in table 5 and got .2679x3=.8037
I then went to table 4, imc, over 40% and the smallest raceway I would be able to use is 1-1/2imc .890
I then need to size my raceway for the remote distribution panel feeders.
My supply house only stocks 1/0,1/0,2 aluminum as 8000 type use-2 or rhh or rhw or rhw-2. i plan on running my own #6 cu ground
I used table 5a for aluminum
1/0=.1963x2=.3926in2
2=.1194in2
The #6egc should be found in table 5 and has an area of .0507 in2
Add all those areas together and you get .5627in2
I went back to table 4 ,rigid pvc sched 80, over 40% and found the smallest race way I could use is 1-1/2 .684
Basically wasn’t sure what table to use for the aluminum conductors I’m using as there are various Charts in table 5 that say rhh,rhw,rhw-2
Thanks I’m advance for any and all help!
Trying to make sure I used right tables to get my pipe fill calculations.
The service entrance conductors will be 3/0 cu thhn/thwn. I used value in table 5 and got .2679x3=.8037
I then went to table 4, imc, over 40% and the smallest raceway I would be able to use is 1-1/2imc .890
I then need to size my raceway for the remote distribution panel feeders.
My supply house only stocks 1/0,1/0,2 aluminum as 8000 type use-2 or rhh or rhw or rhw-2. i plan on running my own #6 cu ground
I used table 5a for aluminum
1/0=.1963x2=.3926in2
2=.1194in2
The #6egc should be found in table 5 and has an area of .0507 in2
Add all those areas together and you get .5627in2
I went back to table 4 ,rigid pvc sched 80, over 40% and found the smallest race way I could use is 1-1/2 .684
Basically wasn’t sure what table to use for the aluminum conductors I’m using as there are various Charts in table 5 that say rhh,rhw,rhw-2
Thanks I’m advance for any and all help!