what 75 C conductors are required for two conductors paralled to carry a load of 925 A.

I come up with 925 / 2 = 463A = (2) 750 kcmil THW. Does the adjustment factor (.8) if they are in the same raceway.
 
Does the adjustment factor (.8) if they are in the same raceway.
Yes, when running all circuit conductors within the same raceway (i.e. it would be at least 4 CCC if 1?, 6 CCC if 3?, assuming conduit is the raceway).
 