dbuckley said:
That is why I asked specifically if the airport - today - serves 777s and A340s which have instant power switchover. Older planes didn't have semiconductor switch, they were mechanical, and hence went through 'off' between onboard and GPU power, hence the cabin lights going out at switchover.
My guess is that planes didn't care about phase sequencing when they had the old way of switching, but with semiconductor static switches doing a no-break changeover then phase sequence is a big issue, as if you cant match phase sequence then the static switch will refuse to switch.
Money still on iWires phase sequence is wrong, until you tell us it works today on a 777 and A340s...
My contact is not aware of any problems with the above planes with respect to the problem being discussed in this thread.
Typical mechanical( non-static switch) transfer switches will transfer between different power sources within 3-4 power cycles.
3 phase rotational loads generally have "lots" of inertia and will not stop in these 3-4 power cycles.
Therefore,if the airport power had reversed phases ,all the A/c breakers would trip each time in all the planes.(ie.3 phase motors don't like a sudden change in the direction of the imposed magnetic field)
I really think it could be something like: voltage T.H.D. limits being exceeded,outside the band of frequency tolerance limits,voltage phase angle problems(not exactly 120 degrees),voltage spikes on the waveform(scr firing problems) etc.
I will be on a crash job in Europe for the next 2 weeks.I will try to answer any other questions when I return.Note:Have not received approval from this customer, as of yet ,to proceed any further with this problem -he is now on the backburner and maybe will be soon off the stove completely.