Im not an electrical engineer or electrician so please take it easy on me! lol I got some good electronics training in the airforce so I know enough to be dangerous.
I work in an injection molding facility and we have been having alot of problems with different things. Motor overloads, modern heat controllers failing to maintain temps, burned breakers, robots cutting off for no apparent reason, computer UPS's switching on and off alot... etc. We have no caps and no filters and our average power factor is .83.
Ive been trying to do some investigating, and I bought a 190-504 Scopemeter so I can check out some waveforms but I wont have it until Friday. Not sure what I can check with it, but Ill learn or sell it if I cant. In the course of trying to figure out what might be going on, I took a look at our supply. We have a 750Kva Transformer (12470GY/7200 : 480Y/277) .... By my calculations (meaning typing it into a calculator I found in google) I'm getting 902 Amps of 480 available. We have Square D switch gear rated at 3000 amps (I assume that means 3000 total and not 1000 per phase???) We have a 230 transformer coming off that 480 main that supplies a pretty good amount of our equipment but I dont know the exact number.
That switch gear has a Micrologic 6.0A and the built in ammeter is currently showing 640 amp, peaking over 720 at some points. I checked it this morning and when I checked we are probably only running at 40-50% production. Some simple napkin math makes me think that when we switch on another 30% of the plant we are going to be bumping the limits of that 900 amp transformer... and maybe that is and has been the problem all along.
I know I need to do a single line, and I need to get all my name plate data together... and that should happen in the next week or two...
Do you guys think Im on the right track? What I really need from you guys is a "heres your smoking gun to get the owner to hire someone to fix it" .... I just have to justify the expense by showing there IS a problem.
thanks everyone
I work in an injection molding facility and we have been having alot of problems with different things. Motor overloads, modern heat controllers failing to maintain temps, burned breakers, robots cutting off for no apparent reason, computer UPS's switching on and off alot... etc. We have no caps and no filters and our average power factor is .83.
Ive been trying to do some investigating, and I bought a 190-504 Scopemeter so I can check out some waveforms but I wont have it until Friday. Not sure what I can check with it, but Ill learn or sell it if I cant. In the course of trying to figure out what might be going on, I took a look at our supply. We have a 750Kva Transformer (12470GY/7200 : 480Y/277) .... By my calculations (meaning typing it into a calculator I found in google) I'm getting 902 Amps of 480 available. We have Square D switch gear rated at 3000 amps (I assume that means 3000 total and not 1000 per phase???) We have a 230 transformer coming off that 480 main that supplies a pretty good amount of our equipment but I dont know the exact number.
That switch gear has a Micrologic 6.0A and the built in ammeter is currently showing 640 amp, peaking over 720 at some points. I checked it this morning and when I checked we are probably only running at 40-50% production. Some simple napkin math makes me think that when we switch on another 30% of the plant we are going to be bumping the limits of that 900 amp transformer... and maybe that is and has been the problem all along.
I know I need to do a single line, and I need to get all my name plate data together... and that should happen in the next week or two...
Do you guys think Im on the right track? What I really need from you guys is a "heres your smoking gun to get the owner to hire someone to fix it" .... I just have to justify the expense by showing there IS a problem.
thanks everyone