- Windsor, CO NEC: 2017
- Hospital Master Electrician
Article 630 applies. Says so right in 630.1 Scope. Electrical-supply-wise, treat it just like an arc welder.
Well the only place any form of the word cut is used in the whole article is 630.1.... :?But the demand factors in 630.11 only apply to arc welders. It doesn't say plasma cutters.
It can be. But it can also be short duration, and intermittent also.I could be wrong, but isn't a cutter more of a constant load than an arc welder?
Does being constant matter?
If you are talking about a continuous load, I would say no, as I doubt the cutter would be used without interruption for three or more hours.
Not that kind of continuous load it has to do with the duty cycle of a welder or a plasma cutter basically the code allows you to cheat and run smaller conductors if the duty cycle is less than 100% you gotta take a look at article 630.
Thanks for clearing up a plasma cutter is not a welder.
what the heck is a "arc welder"
As opposed to a resistance welder, AKA 'spot welders'.
i was being funny
so many types of arc welders. and deep down, all welding is a form or RW, even friction stir, some may use amps, others may not.
Let's try to forget about hammers saws and torches and stick with plasma cutters
Bob,
You don't stick with plasma cutters, you cut with them. I thought you had that one figured out.
I am grappling with a plasma cutter. Is this thing a welder? Does Art. 630 apply? Art. 670?
Supposing I were of a mind to put this thing on a 208V 3-Phase circuit. What on that nameplate do I pay attention to...? :blink:
Oxyacetylene welding isn't resistance welding.