Plastic 4-o nail on round boxes

Status
Not open for further replies.

Jpflex

Electrician big leagues
Location
Victorville
Occupation
Electrician commercial and residential
For illumination purpose with nail on box installed inside building wall but flush with outside wall next to front door. I count find a code that such a box would have to be wet or damp listed.

I did find A code that Lamp holder must be wet listed. 14-2 romex going in plastic box. Is this box legal?
 
For illumination purpose with nail on box installed inside building wall but flush with outside wall next to front door. I count find a code that such a box would have to be wet or damp listed.

I did find A code that Lamp holder must be wet listed. 14-2 romex going in plastic box. Is this box legal?
As far as I know that is does not if it doesn’t extend past the “envelope of home” or exterior of the wall. Although I do often times screw a regular 4” metal octagon to the exterior sheeting where a vinyl J-block is used that has 1 1/2” space within it if it’s not the type of J-block that has an electrical junction incorporated with it.
 