bill@usps06492
Member
- Location
- Connecticut
My neighbor, Jim, just installed a hot tub and did all of the electrical, with alot of over the fence help.He used pvc for the boxes and raceways, but one thing he did, I told him he had to change, was a 120v/20a circuit in AC cable that he ran from his panel to a plastic pull box in the garage( from this point the circuit goes outside through 1"pvc to the tub).He thought that because you can run NM into a metal box that it is okay to run metal into a plastic box.I was taught that because there is no listed fitting for this type of connection and it breaks the ground continuity of the raceway that it cannot be done.He said that because the AC has a seperate insulated ground wire that is spliced with the other circuits ground wire and the AC is connected to the metal panel that it is bonded electrically to the ground.(I did verify this wih an ohmmeter).I have looked in the NEC to find something that deals with this issue, but I cannot come up with anything specific.Any ideas.There was no permit pulled because "as the homeowner I don't need one",Jim informed me after I told him that the inspector would make him change the cable. "No good deed goes unpunished!"