plastic bushings?

Status
Not open for further replies.
what minimum trade size in emt requires a plastic bushing? the code book says that a conduit that has a # 4 or larger wire shall have a bushing. is there no minimum conduit size anymore?
thanks in advance,

Kyle
 

highkvoltage

Senior Member
Re: plastic bushings?

Rule of thumb around here 1" and up for EMT. But common sense should tell you if you are running 1/2" GRS that you need a bushing.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Re: plastic bushings?

See 300.4(F)
(F) Insulated Fittings. Where raceways containing ungrounded conductors 4 AWG or larger enter a cabinet, box enclosure, or raceway, the conductors shall be protected by a substantial fitting providing a smoothly rounded insulating surface, unless the conductors are separated from the fitting or raceway by substantial insulating material that is securely fastened in place.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Re: plastic bushings?

Originally posted by allenwayne:
So a 4/0 al ser cable assys don`t reqire a bushing when enering a panel ??
That's been our practice. For example, if I leave the sheath on a piece of service cable as it runs through a nipple bewteen meter and disconnect, the AHJ doesn't require bushings.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Re: plastic bushings?

That's been our practice. For example, if I leave the sheath on a piece of service cable as it runs through a nipple bewteen meter and disconnect, the AHJ doesn't require bushings.
Larry, since a nipple is a raceway how would this not be a violation?
 