Plastic insulated staples

Status
Not open for further replies.

winnr1

Member
Location
Ohio
Does the n.e.c. state the no. of 12-2 with ground
romex cables that I can secure with a size 1/2"
plastic insulated staple ?
I am having a problem with a local inspector on this,and can not find an answer.
Thanks for your help,opinions.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: Plastic insulated staples

Winnr1, this is more of a listing issue than a code issue.

The packaging of the staples will tell you how many cables are allowed.


Roger
 

tim

Senior Member
Re: Plastic insulated staples

Not sure about the NEC, but we put two 12-2 under one plastic staple laying flat. Your staple manufacture should state on the bag or box what is allowable for the staple in question. Our inspectors have never made this an issue one way or another.
 

winnr1

Member
Location
Ohio
Re: Plastic insulated staples

The plastic bag that contains the staples states,
install according to applicable local Electrical code.No numbers are given and the local inspector is making an issue of this.
Thanks winnr1
 

electricmanscott

Senior Member
Location
Boston, MA
Re: Plastic insulated staples

Only mention of this in NEC is no two cables on edge under one staple. This was a common installation for a while. Here in Mass you are required to use insulated staples with nm cable. I have never had an issue with two cables under one staple.
 

jveiga

New member
Location
Connecticut
Re: Plastic insulated staples

I recieved the following response from Briscon when I e-mailed them. Hope this helps.

"The SN 40 IB staple is UL listed for one 14/2 through 10/3 non metallic sheathed cable.
The SN 150 IB staple is UL listed for two 14/2 through 12/3 non metallic sheathed cables."
 