I had an inspector recently fail an inspection of mine because I did not bond the water heater. I asked him if he was talking about bonding the plastic (pex) water system because I knew I had hooked up the equipment ground. And he said yes and that the only place I could do it was at the water heater because it had copper stub ups and was accessible.
To keep a long conversation short, he said he was waiting on the people at the state gov. to say yey or ney but until then he was requiring it. I didnt arque because I didnt have my code book and he said he didnt either.
Today I had continuing education with one of the white collars who has something to do at the state gov. I asked about this situation. This was his answer in short form:
That it was a good reguirement because the equipmnent ground only bonds the shell of the water heater. And that if the heating element shorted to the water, it would not trip the breaker.
I know that the code only requires metal piping systems likely to become energized to be bonded but does he have a good point? Doesnt fresh water have more resistance than people think and probaly wouldnt trip the breaker anyway? I expected him to call the inspector an idiot so I was shock with his answer.
Opinions please.
To keep a long conversation short, he said he was waiting on the people at the state gov. to say yey or ney but until then he was requiring it. I didnt arque because I didnt have my code book and he said he didnt either.
Today I had continuing education with one of the white collars who has something to do at the state gov. I asked about this situation. This was his answer in short form:
That it was a good reguirement because the equipmnent ground only bonds the shell of the water heater. And that if the heating element shorted to the water, it would not trip the breaker.
I know that the code only requires metal piping systems likely to become energized to be bonded but does he have a good point? Doesnt fresh water have more resistance than people think and probaly wouldnt trip the breaker anyway? I expected him to call the inspector an idiot so I was shock with his answer.
Opinions please.