R Bob said:It sounds as if the 200amp panels are actually sub panels that require an EGC sized per T250.122...#6cu/#4al.
That's the way it sounds to me too.
Also, the equipment grounding conductors for the feeders... from the meter base to the 200A (sub) panels ....should be run with the feeder conductors (250.118) and [250.134(B)]
Basically...if I understand correctly..you bonded to the Grounding Electrode to supply a equipment grounding connection for each 200A (sub) panel...correct?
If so...IMO...thats not allowed.
I take it that the 600A disconnect is part of the Meter bank that also includes the (6) 200A breakers.
If so, the Meter Bank with it's (6) 200A breakers is your service disconnect.
From there, you should have installed 4 wire feeders to the (6) 200A panels.
The 2/0 Cu GEC from the building steel (Grounding Electrode) to the Meter Bank sounds right to me.
Just my opinion
steve