Woah! Let's take a step back here.
The interlocked disconnecting means on an enclosure is to prevent access to live parts in a control enclosure. What else do you have in that cabinet? How did you bring the 120VAC into the cabinet? What type of I/O are you running? Are there terminal strips?
On the surface, cord and plug equipment requires neither a disconnect nor an enclosure. But before I go out on a limb and say you're okay, why do you have a PLC? What's connected to it? Why did you put it in an enclosure in the first place?
I don't think any of those things matter one iota to the original question.
i said the answer is convoluted. First off there is the question of whether he is required to abide by NFPA79 or not.
If he has to abide by it, here is the chain of logic.
6.2.3 When required by 5.3.1.4 you have to have the interlock.
5.3.1.4 If the disconnect is cord and plug, you only have to comply with 6.2.4 and 16.2, so you don't need the interlock if it is plug and cord.
6.2.4 says if it does not have a disconnect it has to require a tool to open the enclosure or the parts inside are separately guarded.
16.2 has to do with signage.
Bob,First off there is the question of whether he is required to abide by NFPA79 or not.
Second off, there is no interlock requirement that comes out in his question. Plug and cord does not require either an enclosure, nor a disconnect if mounted in an enclosure. Section 6.2 only applies to exposed live parts; which is not the case with plug and cord.6.2.3 When required by 5.3.1.4 you have to have the interlock.
Disconnects are not plug and cord but we are loosely taking this to mean "in substitution for" the disconnecting means. Without live parts there is no requirement for the enclosure, a disconnect, nor an interlock. Section 6.2 does not apply.5.3.1.4 If the disconnect is cord and plug, you only have to comply with 6.2.4 and 16.2, so you don't need the interlock if it is plug and cord.
Once again there is no statement of live parts therefore there is no requirement for an enclosure and therefore no interlock and therefore no tool required for access.6.2.4 says if it does not have a disconnect it has to require a tool to open the enclosure or the parts inside are separately guarded.
And therefore no enclosure to paste a sticker on.16.2 has to do with signage.
I thought NFPA 79 was something we always had to comply with when desigining control systems. Are there exceptions?