We are building an industrial control panel, in Australia, for use in Nth Dakota. I have read NFPA79 and UL508A, but would still like some further confirmation / thoughts on the matter, with regards to color coding.
UL508A (66.5) says in "industrial machinery" control panels .....Blue all ungrounded DC conductors, .....White w/Blue stripe all grounded DC conductors.
My usual practice on 24VDC systems is to differentiate between wire function, using colors.
for example:- hard connected positives say Blue, grounded negatives say Grey / Blue stripe, DC inputs say Yellow & DC outputs say Brown. Naturally all wires have numbers as well.
Is this OK, or should I just make all of the inputs & outputs Blue?
Sorry to ask a question that is so similar to those that have been posted before.
Many thanks for your time.
Gavin