We need to install some new service feeder into existing conduit. We have two parallel conduits, but may only fill one for now and keep the second in reserve as a spare. The goal is to get the maximum current capacity (up to 1,000A) using either one or both conduits. Also being considered is whether to select copper or aluminum wire. Final decision will be made by the facility owner based on cost of the wire and other factors.
The conduit is buried 4" Sch-40 PVC, and the run is 360 feet long. Our service is 480V 3-phase wye. The OCPD at the main switch gear uses a rating plug and can be set to 600, 700, 800, 900, 1000, or 1200 amps. Based on demand as reported by the utility, our current maximum load is 80kW (~130A @ 0.75pf), but we want to allow for future load increases. Nonlinear loads do not comprise major portion of our load, therefore NEC 310.15(B)(4)(c) does not apply. Thus the grounded feeder is not considered a current-carrying conductor (CCC).
Option 1: One conduit, 8 copper feeders/conduit, 600A service
Two parallel sets of (4) 400 MCM CU-XHHW-2 feeders.
One #1 CU-XHHW-2 EGC.
Six CCC in raceway, therefore derate to 80%: 380A * 0.8 = 304A/wire * 2 wires/phase = 608A total.
Conduit fill: (8 * 0.843") + (1 * 0.435") = 36.8%
Option 2: Two conduits, 8 aluminum feeders/conduit, 1,000A service
Four parallel sets of (4) 500 MCM compact-stranded AL-XHHW-2 feeders (two parallel sets per conduit).
Two parallel #2/0 CU-XHHW-2 EGC's.
Six CCC in each raceway, therefore derate to 80%: 350A * 0.8 = 280A/wire * 4 wires/phase = 1,120A total.
Conduit fill: (8 * 0.870") + (1 * 0.521") = 39.6%
Option 3: Two conduits, 8 copper feeders/conduit, 1,000A service
Four parallel sets of (4) 300 MCM CU-XHHW-2 feeders (two parallel sets per conduit).
Two parallel #2/0 CU-XHHW-2 EGC's.
Six CCC in each raceway, therefore derate to 80%: 320A * 0.8 = 256A/wire * 4 wires/phase = 1,024A total.
Conduit fill: (8 * 0.748") + (1 * 0.521") = 29.7%
Option 4: Two conduits, 4 copper feeders/conduit, 800A service
Two parallel sets of (4) 600 MCM CU-XHHW-2 feeders (one parallel set per conduit).
Two parallel #1/0 CU-XHHW-2 EGC's.
Three CCC in each raceway, therefore no derating: 420A/wire * 2 wires/phase = 840A total.
Conduit fill: (4 * 1.033") + (1 * 0.477") = 28.1%
Option 5: Two conduits, 4 copper feeders/conduit, 900A service
Two parallel sets of (4) 700 MCM CU-XHHW-2 feeders (one parallel set per conduit).
Two parallel #2/0 CU-XHHW-2 EGC's.
Three CCC in each raceway, therefore no derating: 460A/wire * 2 wires/phase = 920A total.
Conduit fill: (4 * 1.102") + (1 * 0.521") = 32.1%
Thanks!
The conduit is buried 4" Sch-40 PVC, and the run is 360 feet long. Our service is 480V 3-phase wye. The OCPD at the main switch gear uses a rating plug and can be set to 600, 700, 800, 900, 1000, or 1200 amps. Based on demand as reported by the utility, our current maximum load is 80kW (~130A @ 0.75pf), but we want to allow for future load increases. Nonlinear loads do not comprise major portion of our load, therefore NEC 310.15(B)(4)(c) does not apply. Thus the grounded feeder is not considered a current-carrying conductor (CCC).
Option 1: One conduit, 8 copper feeders/conduit, 600A service
Two parallel sets of (4) 400 MCM CU-XHHW-2 feeders.
One #1 CU-XHHW-2 EGC.
Six CCC in raceway, therefore derate to 80%: 380A * 0.8 = 304A/wire * 2 wires/phase = 608A total.
Conduit fill: (8 * 0.843") + (1 * 0.435") = 36.8%
Option 2: Two conduits, 8 aluminum feeders/conduit, 1,000A service
Four parallel sets of (4) 500 MCM compact-stranded AL-XHHW-2 feeders (two parallel sets per conduit).
Two parallel #2/0 CU-XHHW-2 EGC's.
Six CCC in each raceway, therefore derate to 80%: 350A * 0.8 = 280A/wire * 4 wires/phase = 1,120A total.
Conduit fill: (8 * 0.870") + (1 * 0.521") = 39.6%
Option 3: Two conduits, 8 copper feeders/conduit, 1,000A service
Four parallel sets of (4) 300 MCM CU-XHHW-2 feeders (two parallel sets per conduit).
Two parallel #2/0 CU-XHHW-2 EGC's.
Six CCC in each raceway, therefore derate to 80%: 320A * 0.8 = 256A/wire * 4 wires/phase = 1,024A total.
Conduit fill: (8 * 0.748") + (1 * 0.521") = 29.7%
Option 4: Two conduits, 4 copper feeders/conduit, 800A service
Two parallel sets of (4) 600 MCM CU-XHHW-2 feeders (one parallel set per conduit).
Two parallel #1/0 CU-XHHW-2 EGC's.
Three CCC in each raceway, therefore no derating: 420A/wire * 2 wires/phase = 840A total.
Conduit fill: (4 * 1.033") + (1 * 0.477") = 28.1%
Option 5: Two conduits, 4 copper feeders/conduit, 900A service
Two parallel sets of (4) 700 MCM CU-XHHW-2 feeders (one parallel set per conduit).
Two parallel #2/0 CU-XHHW-2 EGC's.
Three CCC in each raceway, therefore no derating: 460A/wire * 2 wires/phase = 920A total.
Conduit fill: (4 * 1.102") + (1 * 0.521") = 32.1%
Thanks!