A residential service calculation.
1200 amp 3 phase 4 wire 480/277v 300' long ,75C thhn cu conductors installed in pvc. 3 sets of parallels, 4 sets of parallels.
I come up with 4 sets of 350 mcm good for 300'
I come up with 3 sets of 600 mcm good for 300'
The engineers say 4 set of 600 mcm.
I think this is over kill.