Clearly the insulation rating of a grounded conductor can be less than that of the phase conductors, in theory. Some examples are: Concentric neutral MV cable only has a thin jacket of the neutral strands, and the neutral/grounded conductor on a MGN distribution system are lower on the pole and have smaller insulators. I cant find any allowance for this in the NEC. In fact, I cant even find anything prohibiting exceeding the voltage rating of a conductor in general, other than 110.3 - did I miss it?
What about single conductor installations in conduit? What considerations would there be in selecting the grounded conductor voltage rating. During a fault, the voltage on the grounded conductor will of course rise, but that is the only condition I can thing of. The specific situation I am thinking of is a 2.4KV circuit with say a 600V grounded conductor.
Edit: also this system would be an outdoor MGN system.
What about single conductor installations in conduit? What considerations would there be in selecting the grounded conductor voltage rating. During a fault, the voltage on the grounded conductor will of course rise, but that is the only condition I can thing of. The specific situation I am thinking of is a 2.4KV circuit with say a 600V grounded conductor.