Please help! Max length of Liquid tight flex

Status
Not open for further replies.

bamiller

Member
I have an inspector that is adament that Liquid tight flex cannot be longer than three (3) feet. The section he is quoting is an exception to the supports required. I would like for him to hear it from someone else.
 

ryan_618

Senior Member
Re: Please help! Max length of Liquid tight flex

metallic or non-metallic? 356.12 limits LFNC to six feet, with a couple of exceptions. 350.12 does not address a length for LFMC. He is quoting the securing, as you stated.
 

bamiller

Member
Re: Please help! Max length of Liquid tight flex

It is nonmetallic liquid tight flex. I thought all sealtight is non-meatalic except for the grounding inside.
 

russ

Senior Member
Location
Burbank IL
Re: Please help! Max length of Liquid tight flex

Is this LFMC Article 350 or LFNC Article 356.
Just curious, where and how is it being used?

Russ
 

bamiller

Member
Re: Please help! Max length of Liquid tight flex

There are two approx. 4 foot pieces feeding two can crushers in a Household waste facility.
 

lrollo

Member
Re: Please help! Max length of Liquid tight flex

As far as I can see in Article 350 of the NEC, there is no maximum length specified. I know I have used it in lengths of up to 100 feet and even buried it. It has to be the inspector is misquoting the code or using his jurisdictional authority. It may aggravate him to be called on it and make more problems than its worth. Can you not get within 3 feet of what you're installing so you can use the flex the way he wants it used? Just thinking sometimes you have to pick your battles and this may not be worth arguing over. Have a great day, Leamon
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: Please help! Max length of Liquid tight flex

Originally posted by bamiller:
It is nonmetallic liquid tight flex. I thought all sealtight is non-meatalic except for the grounding inside.
ARTICLE 350 Liquidtight Flexible Metal Conduit: Type LFMC

350.2 Definition.
Liquidtight Flexible Metal Conduit (LFMC). A raceway of circular cross section having an outer liquidtight, nonmetallic, sunlight-resistant jacket over an inner flexible metal core with associated couplings, connectors, and fittings for the installation of electric conductors.

OR

ARTICLE 356 Liquidtight Flexible Nonmetallic Conduit: Type LFNC

356.2 Definition.
Liquidtight Flexible Nonmetallic Conduit (LFNC). A raceway of circular cross section of various types as follows:

(1)A smooth seamless inner core and cover bonded together and having one or more reinforcement layers between the core and covers, designated as Type LFNC-A

(2)A smooth inner surface with integral reinforcement within the conduit wall, designated as Type LFNC-B

(3)A corrugated internal and external surface without integral reinforcement within the conduit wall, designated as LFNC-C.
 

russ

Senior Member
Location
Burbank IL
Re: Please help! Max length of Liquid tight flex

I've read 356 .10,.12 and.30 back and forth, and it looks like you can have up to six feet (356.12 (3)) but it would have to be straped, 356.30.

Russ
 

russ

Senior Member
Location
Burbank IL
Re: Please help! Max length of Liquid tight flex

I,ve been allowing longer than 3ft whips of LFMC (We don't allow LFNC) for a long time. Guess maybe I been a little lenient :D and I thought I was tough!
 

ryan_618

Senior Member
Re: Please help! Max length of Liquid tight flex

Originally posted by russ:
I,ve been allowing longer than 3ft whips of LFMC (We don't allow LFNC) for a long time. Guess maybe I been a little lenient :D and I thought I was tough!
Why wouldn't you allow it?
 

russ

Senior Member
Location
Burbank IL
Re: Please help! Max length of Liquid tight flex

It's possible it could be used, but not likely.

From the Chicago Code

PART B. LIQUIDTIGHT FLEXIBLE NONMETALLIC CONDUIT

18-27-351.23.
Use. (a) Permitted. Listed liquidtight flexible nonmetallic conduit shall be permitted to be used only in corrosive areas, with special
permission, in installations where no suitable alternative wiring material can be used.
FPN: Extreme cold may cause some types of nonmetallic conduits to become brittle and therefore more susceptible to damage from physical
contact.
 

pierre

Senior Member
Re: Please help! Max length of Liquid tight flex

If you were to run an EGC in the liquidtight (metallic or nonmetallic), there is no limit to the length it is installed.
LFNC-B is the gray colored type that most of see today. The UL White Book (General Information for Electrical Equipment) describes the different types and permitted listings.

Pierre
 

ryan_618

Senior Member
Re: Please help! Max length of Liquid tight flex

Pierre, take a look at 356.12 again. As you'll notice, it is not an EGC issue. See also 250.118 for types of EGC's permitted. The only exceptions (I don't have my code here, but I think I remember) are: 1) if you absolutley need it for flexibility or 2) If it somes pre-wired in a coil of some sort.
 

curt swartz

Electrical Contractor - San Jose, CA
Location
San Jose, CA
Occupation
Electrical Contractor
Re: Please help! Max length of Liquid tight flex

Ryan

Look at 356.10(5). I believe there is an error in 356.12(3) since there isn't a 356.100(5). It should be 356.10(5)
 
A

a.wayne3@verizon.net

Guest
Re: Please help! Max length of Liquid tight flex

As long as it is strapped in accordance with nec
IE: within required distances of box and between straps ,there is no max. distance,just a max. length of whip 6 ft.
After all it is conduit.......
 

gwz2

Senior Member
Location
Indiana
Re: Please help! Max length of Liquid tight flex

That " in accordance with the NEC"

includes 356.60 which refers to 250.134(B) and to 250.102.
 

russ

Senior Member
Location
Burbank IL
Re: Please help! Max length of Liquid tight flex

I'm A convert!
I believe Curt is right about the miss print on the code number.

You guys have figured out the whip length.

My vote.
A six foot whip (or less) with a proper ground should be acceptable, more than six foot the straping comes in.

Russ
 

ryan_618

Senior Member
Re: Please help! Max length of Liquid tight flex

Originally posted by russ:
I'm A convert!
I believe Curt is right about the miss print on the code number.

You guys have figured out the whip length.

My vote.
A six foot whip (or less) with a proper ground should be acceptable, more than six foot the straping comes in.

Russ
Ditto!!!
The NEC is a difficult article enough to read and fully understand without misprints like this!!! Oh well, we learn once again.
Nice catch on the misprint.
 

eprice

Senior Member
Location
Utah
Re: Please help! Max length of Liquid tight flex

Well, I agree partially. Yes, the errata indicates that the reference in 356.12(3) should be to 356.10(5) rather than 356.100(5), but this only allows LFNC-B to be used in lengths longer than 6'. I believe other types of LFNC are limited by 356.12(3) to lengths of 6' unless a longer length is approved as essential for a required degree of flexibility. Since LFNC-B is available, why would it ever be necessary to approve the use of another type in lengths longer than 6'?
 