Hi all. I'm so unsure of myself right now. Can't wrap my head around grounding and bonding transformers. I've done panels, GFCI's, AFCI's, hundreds of lights, and helped on two PV installs. Transformers are so confusing to me. I'm not installing one but i am trying to understand the proper way before i actually have to one day. I'm sure ill get to watch someone first but it would be nice not to be clueless when i do see it done. Lets say i'm working with a 3-Phase, 4-Wire 480Y/277 V system and want to install a 75KVA transformer and 200amp panel.
Primary Side grounding/bonding
Using a 75KVA 480 primary 120/208 secondary transformer.
Come off 125A MCB at switch gear. 90amps*1.25= 112.5 OCP device. Is This Correct?
75000/(480*1.73)=90 90*1.25=112.5 USING 75 degree column i use 2awg. Is this Correct?
I pull 3 2awg THHN wires, phase them brown, orange, and yellow.
Since i'm using EMT i do not have to run a wire for the equipment grounding conductor. Under 250.122 it is considered an EGC. Is this correct? Is that all on the primary side i have to do?
200A 208Y/120 three phase panel with a 200A main. Main in panel will serve as OCP and taps from transformer are under 10 feet in lenght.
I run 350 kcmil X1-A Phase, X2-B phase, X3-C Phase X0-Neutral Bar of panel
75000/(208*1.73)=208A 208*1.25=260A size secondary conductors need to be?
Using 90 degree column and derating for 4 conductors (neutral is considered current carrying in this)
350kcmil 350A*0.8=280A Is this correct?
Secondary grounding/bonding (system Bonding Jumper At transformer only)
Grounding electrode-Connect to X0 to ibeam (250.66) 2awg
Supply Side Bonding Jumper- using EMT this is my SSBJ. Is this correct? Is using an LB ok or does it all have to be EMT?
System Bonding Jumper- X0 to case of transformer and to ground bar of panel. (no neutral to ground connection in panel) Is this correct?
I feel like i'm missing something. Any help would be greatly appreciated.
Primary Side grounding/bonding
Using a 75KVA 480 primary 120/208 secondary transformer.
Come off 125A MCB at switch gear. 90amps*1.25= 112.5 OCP device. Is This Correct?
75000/(480*1.73)=90 90*1.25=112.5 USING 75 degree column i use 2awg. Is this Correct?
I pull 3 2awg THHN wires, phase them brown, orange, and yellow.
Since i'm using EMT i do not have to run a wire for the equipment grounding conductor. Under 250.122 it is considered an EGC. Is this correct? Is that all on the primary side i have to do?
200A 208Y/120 three phase panel with a 200A main. Main in panel will serve as OCP and taps from transformer are under 10 feet in lenght.
I run 350 kcmil X1-A Phase, X2-B phase, X3-C Phase X0-Neutral Bar of panel
75000/(208*1.73)=208A 208*1.25=260A size secondary conductors need to be?
Using 90 degree column and derating for 4 conductors (neutral is considered current carrying in this)
350kcmil 350A*0.8=280A Is this correct?
Secondary grounding/bonding (system Bonding Jumper At transformer only)
Grounding electrode-Connect to X0 to ibeam (250.66) 2awg
Supply Side Bonding Jumper- using EMT this is my SSBJ. Is this correct? Is using an LB ok or does it all have to be EMT?
System Bonding Jumper- X0 to case of transformer and to ground bar of panel. (no neutral to ground connection in panel) Is this correct?
I feel like i'm missing something. Any help would be greatly appreciated.