P papanick New member Jun 16, 2004 #1 Are there any code requirements for the labeling and/or testing of lighting fixtures when they installed in a return air plenum HVAC system. This is not a question for any fire rated assemblies appliations.
Are there any code requirements for the labeling and/or testing of lighting fixtures when they installed in a return air plenum HVAC system. This is not a question for any fire rated assemblies appliations.
ryan_618 Senior Member Location Salt Lake City, Utah Jun 16, 2004 #2 Re: Plenum approved lighting fixtures They must have a flame spread index of not more than 25 and a smoke developed index of not more than 50. This shouldn't be a problem if they are made of steel.
Re: Plenum approved lighting fixtures They must have a flame spread index of not more than 25 and a smoke developed index of not more than 50. This shouldn't be a problem if they are made of steel.
E esox39 Member Location Chicago, IL Jun 16, 2004 #3 Re: Plenum approved lighting fixtures 300.22(b)......enclosed gasket-type luminaires (fixtue) shall be permitted. These fixtures are commonly call "plenum rated".