Plenum Cable Use

Status
Not open for further replies.
NEC Sec 300-22 ( C ) ( D ) states that UL listed cable is rated for indoor Air Handling Spaces I have a UL Listing ( 9c45 ) and have an Inspector Questioning the color of the cable TIEWRAP as the Plenum rate or not and not the UL listing . I find this quite peculiar and am having trouble convincing the Inspector . Any suggestions ?
 

JohnJ0906

Senior Member
Location
Baltimore, MD
I think that most plenum rated tie-wraps are black. If he sees ones that are white, he might think that they are not plenum rated.

If what you installed is plenum rated, leave a package for him to see.
 

DUCKMAN

Member
Plenum Tie-wraps

Plenum Tie-wraps

Where in the code does actually require the use of a plenum rated tie-wrap???
 

DUCKMAN

Member
Tie-Wraps

Tie-Wraps

hbiss said:
The NEC has nothing to say about plastics in plenum spaces other than LV wiring. I believe that this is a local and building code issue.

-Hal

I keep hearing about it, but I have yet to see an actual requirement, which is why I asked. I am in Mass, and I cannot recall seeing anything about tie-wraps in the building code, and have never seen anything in the NEC.

Anyone else have a thought???
 