Plenum Ceilings Junction box and conduit fittings

Fordean

Senior Member
Location
New Jersey
Occupation
Electrical Contractor
Just curious
Plenum ceiling usually use the MC type cable and emt. 4 11/16 box where needed.

The Plenum rated boxes. Don't have a ground screw hole to keep plenum seal. How do they ground box, With no tailing. Grounded Locking ring with screw?

Also, EMT fittings. Are there a specific type. For plenum. Like Set screw should or should not be used. And only Compression type?

MC cabling not a issue. But if you use a MC connector above ceiling. Is that ok? Just looking to avoid inspection issues. Seems things are really getting stricter.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
The primary requirement is simply metallic wiring methods.
Beyond that there are no restrictions.
Most, if not all, 4" and 4-11/16 have a threaded spot for a ground screw.
Under today's energy codes a plenum ceiling would be rare I'm told.
 

Fordean

Senior Member
Location
New Jersey
Occupation
Electrical Contractor
The primary requirement is simply metallic wiring methods.
Beyond that there are no restrictions.
Most, if not all, 4" and 4-11/16 have a threaded spot for a ground screw.
Under today's energy codes a plenum ceiling would be rare I'm told.
Appreciate the response. But I know about the screw. I worry a inspector that may have a strict standard. Attached is a spec of a Plenum type of box. They have no screws. Don't know how long this has been around. But I never used one, Even in past installs.
 

Attachments

  • 226.pdf
    113.9 KB · Views: 11

Fordean

Senior Member
Location
New Jersey
Occupation
Electrical Contractor
I cannot think of a location where those would be required except maybe in Chicago.
I never used them. Just all metal wiring/conduit But i do use Plenum rated Cat 6. I see many not use Plenum low volts but would hate to have to change.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
As far as I know, the only place that requires a plenum rated box is Chicago. They also require the use of flexible metal tubing in plenum ceilings...another thing that is pretty much only used in Chicago.
 