where can I find plenum rated receptacles for above a dropped ceiling which is used for a return air?
You can just use a regular receptacle. Problem is the code does not let you use it as you can't have flexible cords above a drop ceiling.where can I find plenum rated receptacles for above a dropped ceiling which is used for a return air?
this I know...however our state inspector informed me there is a product out there that encases the cordand receptacle therefore legalwhere can I find plenum rated receptacles for above a dropped ceiling which is used for a return air?
I thought wall-warts were okay since they have no line-voltage cord.You can just use a regular receptacle. Problem is the code does not let you use it as you can't have flexible cords above a drop ceiling.
If your state inspector finds it let us know. Besides the issue with flexible cords above any ceiling very few things are allowed in plenums.this I know...however our state inspector informed me there is a product out there that encases the cordand receptacle therefore legal
Required in Chicago for plenum ceilings along with flexible metal tubing (Article 360)...one of the few places you ever see flexible metal tubingMaybe the inspector was talking about this? Still wouldn’t make it compliant.View attachment 2551553
That’s kinda weird combination! Many years ago we wired a mall in Charleston, SC, I believe, and they would not allow MC cable. Doesn’t Chicago also require houses to be wired in type ac or mc type wiring method? NM not allowed?Required in Chicago for plenum ceilings along with flexible metal tubing (Article 360)...one of the few places you ever see flexible metal tubing
hillbilly1 said:Maybe the inspector was talking about this? Still wouldn’t make it compliant. (Picture of a 1900 box)
hillbilly1 said:Doesn’t Chicago also require houses to be wired in type ac or mc type wiring method? NM not allowed?
No, in that it is not constructed for the primary purpose of routing air, but the code explicitly applies some plenum rules to those "other environmental air" spaces.Is a space above the ceiling used for a return air really a plenum?
I did a house in emt, the electrician that the builder normally used couldn’t run conduit, so I did it as a favor. Not easy in wood construction. The home owner requested it because he wanted to be able to pull out any wire that might go “bad” and pull in new. LOL!Why would anybody even think to use a plastic box in a return air space??
Not quite! They require EMT!!
-Hal
Thats what electricians call it, but the plenum is inside a metal air duct. NEC finally got it right a couple of code cycles ago and called it other space for environmental air. Just go to your wholesale house and ask for some "other space for environmental air" rated cableIs a space above the ceiling used for a return air really a plenum?
A plenum does not have to be metal or metal lined, although they often are. It just has to constructed separate from other spaces for the primary purpose of carrying air.Thats what electricians call it, but the plenum is inside a metal air duct. NEC finally got it right a couple of code cycles ago and called it other space for environmental air. Just go to your wholesale house and ask for some "other space for environmental air" rated cable
If I had to wire a house in EMT, there would be mostly single vertical runs and lots of J-boxes in the attic and crawl spaces.