When running Class 2 / Class 3 / CM cable inside a metal conduit in an air return plenum above a suspended ceiling, is plenum rated cable required inside that metal conduit?
Here's what confuses me:
From my 2008 Handbook:
725.154(A) Plenums. Cables installed…shall be Type CL2P or CL3P. Listed wires and cables installed in compliance with 300.22 shall be permitted. Listed plenum signaling raceways shall be permitted to be installed in other spaces used for environmental air as described in 300.22(C). Only Type CL2P or CL3P cable shall be permitted to be installed in these raceways.
From Mike’s Understanding the NEC, 2008 edition:
725.154(A) Ducts, Plenums, and Other Space Used for Environmental Air.
Class 2 and Class 3 cables not identified as suitable for plenum use can be installed above a suspended ceiling or below a raised floor used for environmental air if the cable is installed in a metal raceway [300.22(C)(1)].
The text from my 2008 Handbook is very different from Mike's 2008 publication.
What am I missing here? Do I need plenum rated cable inside the metal conduit that's run in the plenum?
Here's what confuses me:
From my 2008 Handbook:
725.154(A) Plenums. Cables installed…shall be Type CL2P or CL3P. Listed wires and cables installed in compliance with 300.22 shall be permitted. Listed plenum signaling raceways shall be permitted to be installed in other spaces used for environmental air as described in 300.22(C). Only Type CL2P or CL3P cable shall be permitted to be installed in these raceways.
From Mike’s Understanding the NEC, 2008 edition:
725.154(A) Ducts, Plenums, and Other Space Used for Environmental Air.
Class 2 and Class 3 cables not identified as suitable for plenum use can be installed above a suspended ceiling or below a raised floor used for environmental air if the cable is installed in a metal raceway [300.22(C)(1)].
The text from my 2008 Handbook is very different from Mike's 2008 publication.
What am I missing here? Do I need plenum rated cable inside the metal conduit that's run in the plenum?