Thanks Bryan,
Then if looking at:
(1) Cord-and-Plug-Connected Equipment Not Fastened
in Place. The rating of any one cord-and-plug-connected
utilization equipment not fastened in place shall not exceed
80 percent of the branch-circuit ampere rating.
What is the "rating" of a motor?
The rating of the motor is the rated ampacity(FLA) and voltage of the motor.
...if the plug and receptacle are not used as a motor disconnect?
Standard 15 amp receptacles are rated for 1/2 hp and 20 amp ones are rated for 1 hp per the UL Guide Information for Receptacles for Plugs and Attachment Plugswhat do you do for a garage door opener?
A cord-and-plug comnnection is by a nature a means of disconnect, whether it is designated that way or not. You may be providing another means of disconnect as required by the NEC but it would be in addition to the cord-and-plug disconnecting means...
What about my JET table saw that comes with a 1-1/2Hp motor rated 115VAC, 12A and is furnished with a NEMA 5-15P plug and a HP rated disconnect switch?
I don't understand your question?
Take for example a typical electrical system. From service point to equipment, you may several disconnecting means. Service Disconnect, Feeder Disconnect, Branch-Circuit Disconnect, Switch, Cord-and-Plug Connection. Which one is the disconnecting means? ALL OF THEM...
In the JET saw example the disconnect switch would start stop the motor, not the cord plug.
What about my JET table saw that comes with a 1-1/2Hp motor rated 115VAC, 12A and is furnished with a NEMA 5-15P plug and a HP rated disconnect switch?
What about my JET table saw that comes with a 1-1/2Hp motor rated 115VAC, 12A and is furnished with a NEMA 5-15P plug and a HP rated disconnect switch?
According to 430.248 you saw motor is actually less than 3/4 HP with an FLA of 12 amps.