Plug-in Busway in a Class II Div 2 Area

Status
Not open for further replies.
No, it isn't a recognized wiring method in Class II. See Sections 368.12(C) and 502.10(B).

That said, is the busway actually in the classified location?
 
Can I install a plug-in busway in a Class II Div. 2 area about 10 feet off the floor in a high bay area?

  1. The elevation is immaterial. Either the area 10' AFF is classified or unclassified.
  2. You can install the busway if it is LISTED for the Class and Division and Group. (Highly unlikely.)
  3. You would certainly unlikely to be able to use its 'pluggability' feature while energized AND while the area remains Classified. :lol:
 