fifty60 Senior Member Location USA Jan 10, 2014 #1 Does equipment that plugs into a 20A outlet have to have an SCCR?
petersonra Senior Member Location Northern illinois Occupation engineer Jan 10, 2014 #2 fifty60 said: Does equipment that plugs into a 20A outlet have to have an SCCR? Click to expand... No. Unless it is a SPD or an industrial control panel.
fifty60 said: Does equipment that plugs into a 20A outlet have to have an SCCR? Click to expand... No. Unless it is a SPD or an industrial control panel.
petersonra Senior Member Location Northern illinois Occupation engineer Jan 10, 2014 #4 fifty60 said: What is an SPD? Click to expand... Surge Protection Device. I looked this up. It says only permanently installed SPD are required to be listed and have a SCCR. I don't see how anything that is plugged in and is portable can be considered permanently installed.
fifty60 said: What is an SPD? Click to expand... Surge Protection Device. I looked this up. It says only permanently installed SPD are required to be listed and have a SCCR. I don't see how anything that is plugged in and is portable can be considered permanently installed.