I have often thought this was one of the safest places to put corded equipment. Wonder what their thinking was on this when they wrote it.charlie b said:If by "plugged" you mean there will be a flexible cord with a cord cap and you intend to plug it into a standard receptacle outlet, no this is not allowed. NEC article 400.8(5) forbids the use of flexible cords above a suspended ceiling.
petersonra said:I have often thought this was one of the safest places to put corded equipment. Wonder what their thinking was on this when they wrote it.
stickboy1375 said:Because the cord will dry rot and crack.
stickboy1375 said:Because the cord will dry rot and crack.
JohnJ0906 said:http://i125.photobucket.com/albums/p66/JohnJ0906/HPIM0455.jpg
http://i125.photobucket.com/albums/p66/JohnJ0906/HPIM0456.jpg
http://i125.photobucket.com/albums/p66/JohnJ0906/HPIM0458.jpg
Here are a few shots of a cord that spent a few years in a ceiling. This is the part that I stripped - this was inside the cord jacket, and still had rotten insulation.
stickboy1375 said:Nice pics John... I always picture the ceiling grid becoming energized with cords in the ceiling... that would be a nice surprise. :roll:
jrdsg said:Is the receptacle above the ceiling tile a code violation itself?
This is a common violation. Overhead projectors, condensate pumps.. common or not ,it is still a violation.stickboy1375 said:No, its when you plug a cord in, then its a violation. 400.8 (5)
ItsHot said:This is a common violation. Overhead projectors, condensate pumps.. common or not ,it is still a violation.