Is it a code violation to have a cord plugged into a load side of UPS feeding a junction box where cord is terminated and THHN conductors extended through conduit to receptacles downstream.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Welcome to the forum.

You're basically asking whether in-wall premises wiring can be supplied by a plug and cord.

I think yes, since this is the basis of generator inlets, as well as many audio/video installations.
 

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
IMHO the violation might be the cord with the male cap coming out of the junction box. This makes the flexible cord a permanent part of the building wiring.

If instead you have a male inlet on the wall, I think the setup is fine.