Sorry, but no. Just no.There is a neutral lug on the breaker to attach the load neutral.
If the panel has no corresponding neutral bus, ignore the breaker's neutral terminal and land the white wire normally.There is a neutral lug on the breaker to attach the load neutral.
That is only for the load side. It will not work because the CB is expecting the line side connection from the bus. Your circuit will have no neutral.There is a neutral lug on the breaker to attach the load neutral.
No, a plug-on neutral breaker has a load neutral terminal like a GFCI, but no line-side pigtail.If the breaker has a plug-on neutral and a separate terminal for a neutral, it must be some kind of AFCI/GFCI breaker.
The AFCI requires a connection to service neutral to provide power for the internal circuit board. But the GFCI needs the neutral to see the potential loss to ground of current.Thanks all. I clearly needed to read up on how GFCI/AFCI breakers work.
I think it's ok if you switch both at the same time ?This method of manufacturing of course violates the code prohibitions of switching neutral connections to a load.............
Just sayin..........