Trying to find code to reference if allowable or not allowed?
I have a 3 pole 30-amp breaker feeding a L15-20R with #10 wiring. From there we are plugging in a PDU in a data rack that has several receptacles and an internal circuit breaker within the PDU.
Please reference code if able.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
The single receptacle would need to be 30 amps or larger to be on a 30 amp circuit. Someone will post the code section.
 