Plugmold Question

Status
Not open for further replies.

Amps

Electrical Contractor
Location
New Jersey
Occupation
Electrical, Security, Networks and Everything Else.
Attended a 2020 Code seminar and one topic was countertop and work surface receptacles, 210.52. (C) (2) (A). It was determined that the receptacle requirement for a large island or peninsula (depending on dimensions) could be met by ganging 2 or 3 receptacles in one box to avoid cutting multiple holes in cabinets. Plugmold came up and there was a comment that all of the receptacles in the plugmold cannot be counted, and that X amount of feet of plugmold equals one receptacle. Does anyone know if this is true and have a source to refer to? Thanks in advance.
 

HEYDOG

Senior Member
If you are referring to a multi outlet assembly…..look at 210.52(c). All the way down in right hand column on page 68 in 2020 NEC.
 

Amps

Electrical Contractor
Location
New Jersey
Occupation
Electrical, Security, Networks and Everything Else.
If you are referring to a multi outlet assembly…..look at 210.52(c). All the way down in right hand column on page 68 in 2020 NEC.
You nailed it! Thank you very much!
 