Good morning everyone,
I was just having a discussion with a coworker who does commercial. He was explaining that I made an error by adding a light to an existing circuit that was servicing outlets in a commercial office space. I told him that there were only 6 outlets on the circuit and therefore the loading was not a problem. He said that in commercial you cannot have receptacles and lighting on the same circuit. I didn't know this so I asked for the code reference so I can understand it, but he couldn't tell me the code reference off the top of his head and I couldn't find it. Does anyone know what the code section pertaining to this is?
I thought that 220.13 was telling me specifically that I COULD do this, but perhaps that is just for calculation purposes.
"In other than dwelling units, receptacle loads of computed at not more that 180va per outlet accordance with 220.3(B)(9)...shall be permitted to be added to the lighting loads abd made subject to the demand factors given in table 210.11..."
I was just having a discussion with a coworker who does commercial. He was explaining that I made an error by adding a light to an existing circuit that was servicing outlets in a commercial office space. I told him that there were only 6 outlets on the circuit and therefore the loading was not a problem. He said that in commercial you cannot have receptacles and lighting on the same circuit. I didn't know this so I asked for the code reference so I can understand it, but he couldn't tell me the code reference off the top of his head and I couldn't find it. Does anyone know what the code section pertaining to this is?
I thought that 220.13 was telling me specifically that I COULD do this, but perhaps that is just for calculation purposes.
"In other than dwelling units, receptacle loads of computed at not more that 180va per outlet accordance with 220.3(B)(9)...shall be permitted to be added to the lighting loads abd made subject to the demand factors given in table 210.11..."