2-203 Log #1391 NEC-P02 Final Action: Reject
(210.52(B)(2) Exception No. 3 (New))
____________________________________________________________
Submitter: George Stolz, II, Pierce, CO
Recommendation: Add an Exception to (B)(2) to read:
Exception No. 3: Receptacles installed on an island or peninsula to serve other areas in compliance with the requirements of 210.52(A)(1) and (2) shall be permitted on the same small appliance branch circuit(s) installed to comply with 210.52(C)(2) or (3).
Substantiation: Islands and peninsulas that are adjacent to living areas not covered under the provisions of 210.52(B) sometimes require an installation of a 15 or 20 amp receptacle to conform with 210.52(A)(2)(3). There is the risk of a “living room” outlet that is not required to be GFCI protected being installed in a location where GFI protection is required on the 20 amp circuit installed per 210.52(C)(2) or (3).
In addition, given that the use of said receptacles is remote, it should be acceptable to allow a receptacle that is on an island to serve an adjacent “living room.” It doesn’t seem to constitute a high potential for load, and is generally installed for code’s sake, not because a true need is perceived by the installer or AHJ.
Panel Meeting Action: Reject
Panel Statement: The receptacles in the adjacent room should not be permitted on the small appliance branch circuit. Some of the arrangements encountered would fit well into the submitter’s concept, but others may indeed place a burden on the small appliance branch circuit. Given the wide and varying types of construction, it is prudent to keep the receptacles delineated between the two rooms.