A portion of the walk had to be removed for the plumber on a commercial pool. The plumber cut through the grounding grid. After the plumber fixed his run they called me and wanted me to cad weld the grid back. I thought that the grid could be put back together with direct burial ground connectors. Code references would be appreciated.
a portion of the walk had to be removed for the plumber on a commercial pool. The plumber cut through the grounding grid. After the plumber fixed his run they called me and wanted me to cad weld the grid back. I thought that the grid could be put back together with direct burial ground connectors. Code references would be appreciated.
680.26 (b), (c)???
Who asked you to cad weld it?
680.26 (b), (c)???
680.26(B) Bonded Parts.
The parts specified in 680.26(B)(1) through (B)(7) shall be bonded together using solid copper conductors, insulated covered, or bare, not smaller than 8 AWG or with rigid metal conduit of brass or other identified corrosion-resistant metal. Connections to bonded parts shall be made in accordance with 250.8. An 8 AWG or larger solid copper bonding conductor provided to reduce voltage gradients in the pool area shall not be required to be extended or attached to remote panelboards, service equipment, or electrodes.
250.8 Connection of Grounding and Bonding Equipment.
(A) Permitted Methods. Grounding conductors and bonding jumpers shall be connected by one of the following means:
(1) Listed pressure connectors
(2) Terminal bars
(3) Pressure connectors listed as grounding and bonding equipment
(4) Exothermic welding process
(5) Machine screw-type fasteners that engage not less than two threads or are secured with a nut
(6) Thread-forming machine screws that engage not less than two threads in the enclosure
(7) Connections that are part of a listed assembly
(8) Other listed means