Plumber gets wacked cutting water line

Status
Not open for further replies.

jaykilty

Member
Location
mass
Heard from a plumber I work with today and was told that after cutting the main water line on the house side of the water meter he received a shock bad enough to knock him off his feet. I asked him if the GEC was still connected to both the street and the home and he said it was. I can only guess that the GEC was still connected at the main. I was not there. He wanted to know how this could happen, and I couldn't answer his question. Also it started a fire on the 2nd floor of the home. What caused this?
 
Heard from a plumber I work with today and was told that after cutting the main water line on the house side of the water meter he received a shock bad enough to knock him off his feet. I asked him if the GEC was still connected to both the street and the home and he said it was. I can only guess that the GEC was still connected at the main. I was not there. He wanted to know how this could happen, and I couldn't answer his question. Also it started a fire on the 2nd floor of the home. What caused this?
The service neutral is open or has a very high resistance. The water pipe, because of its connections to other buildings in the area and their water pipe bonding connections, was serving as the neutral. When he cut the pipe and was touching both ends, he was serving as the neutral.
 
I agree with Don. If the GEC connection to a common water system is sound then an open neutral can go undetected for a long time because as Don mentioned the neutral current will flow into the neighbors building and back to the source.
 
I agree with Don. If the GEC connection to a common water system is sound then an open neutral can go undetected for a long time because as Don mentioned the neutral current will flow into the neighbors building and back to the source.

I have some pics somewhere of a service drop to a house with the neutral broken right off, the triplex was hanging by the hot wires. The neutral snapped when a car hit the pole the triplex was attached to. We were next door repairing a mast that was bent over because the pole had snapped. The POCO just guyed the pole and left it. This had been this way for nearly two years while the owner of the bent mast battled with her insurance company over the repair, which meant the service be moved.

The POCO did fix the open neutral a couple days after I called it in.
 
I have some pics somewhere of a service drop to a house with the neutral broken right off, the triplex was hanging by the hot wires. The neutral snapped when a car hit the pole the triplex was attached to. We were next door repairing a mast that was bent over because the pole had snapped. The POCO just guyed the pole and left it. This had been this way for nearly two years while the owner of the bent mast battled with her insurance company over the repair, which meant the service be moved.

The POCO did fix the open neutral a couple days after I called it in.

My guess is that this happens more than we think. As long as the pipe clamp isn't corroded these can remain for, as you've stated, years without detection.
 
I told my plumbing acquaintances that they should use a jumper cable when cutting those lines. I think it fell on deaf ears
 
Great advice I will pass that along to the plumber. Any idea about cause of fire
The open neutral creates a series parallel circuit with higher than normal voltage on one side and lower than normal on the other side. This often lets the smoke out of electronic equipment and sometimes results in a fire.
 
My guess is that this happens more than we think. As long as the pipe clamp isn't corroded these can remain for, as you've stated, years without detection.
The was a paper from the American Waterworks Association a number of years ago that said, on average, this happens about once a day in the US.
 
or somebody elses N was using that pipe and he just so happened to re-bridge that gap?
 
There is a great video on this from the city of Miami fire dept. I don't have a link. maybe mike holt has it on his web site
 
My guess is when he cut the pipe then they completely lost the neutral and a tv or radio or such upstairs blew and caused the fire.


yup. this close to the election, if you don't have a really good ground on the tv,
the spew coming from the candidates will destroy the set.

if you are tuned to fox news, i'm told it's almost instantaneous. :angel:
 
I think what has been said above is what likely happened .....

Interesting story though, had a utility come connect a service for me once while the plumber was working on copper lines.

Heard him shouting when they energized. Utility swapped L-G at the meter. Linemen were staring at each other in disbelief.


Sent from my iPhone using Tapatalk
 